Test Sheet Madness

Talk Electrician Forum

Help Support Talk Electrician Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.
http://i316.photobucket.com/albums/m...ert_Page_3.jpg

1. 6mm cable often has a 2.5mm cpc

2. 5 second diss time at 80A (if it was true)

3. 61008 would not be type B. Even though rated at 80A the rate is not overcurrent protection.

4. Where are the usually 6KA Capacity ratings?

5. Shouldn't they be ditto marks under the "30mA" not / marks

6. No R1+R2 for the ring circuit

7. The best bit..The explanation he has written that"> = GREATER THAN"....LOL

8. Zs on the sockets at 0.3 is less the Ze at 0.35

9. The Cooker seems very close to the DB at 0.01ohms as well as the lights at 0.02ohms

10.The Zs's dont work out (taking p'paths into account)

11.Why are the X1 times not all the same, and what about X5 times?

12.Designation of the DB is not DB1 as expected, but BSEN60439-3

13.240/0.35=686Amps ie; nowhere near 16KA

14.He cannot even spell cupboard.

15.As well as his MFT he seems to have got all his test gear out that day including his electrode tester.

ARE THERE ANY MORE

http://i316.photobucket.com/albums/m...ert_Page_2.jpg

1. U 230V Uo 240V why are they different?

2. 16KA PFC again

3. 1361 Type "cartridge" ? at 8KA ?

4. was it really 16mm bonding cable ?

5. 61008...Number of poles "1"

6. Presence of diagrams?

7. Earth electrode TESTED

8. Verification of phase sequence TESTED

9. Verification of volt drop TESTED (i very much doubt it)

ANY MORE?

http://i316.photobucket.com/albums/m...ert_Page_1.jpg

1. Not a lot of faith in his own install.......He only gave it 3years for the next inspection.

ANY MORE?

 