Good afternoon all,
I was after a bit of advice, i have just came across some Crabtree C50's for the first time, i believe them to be the old 3kA type (white writing and an old installation).
The MCB is a 50A 3 Phase, the problem is we are installing a new distribution board in another part of the plant and the only place to take the supply from is this 50A C50. due to it only being 3kA, is there a way i can get past this?
i cant just simply remove this as its in an enourmous Distribution board.
i have looked at 434.5.1 which states : -
"except where the following paragraph applies, the rated short circuit breaking capacity of each device shall be not less than the maximum prospective fault current at the point at which the device is installed.
A lower breaking capacity is permitted if another protective device or devices having the necessary rated short circuit breaking capacity is installed on the supply side. In this situation the characteristics of the devices shall be co-ordinated so that th energy let-through of these devices does not exceed that which can be withstood, without damage, by the device(s) on the load side."
The problem i am having is knowing if using an MG (Schneider) Distribution board filled with Multi9 MCB's will meet this requirement.
i have spoken to electrium and all they have advised is i see if 434.5.1 can help.
any advice would be gratefully appreciated. Thanks in advance
Peter
I was after a bit of advice, i have just came across some Crabtree C50's for the first time, i believe them to be the old 3kA type (white writing and an old installation).
The MCB is a 50A 3 Phase, the problem is we are installing a new distribution board in another part of the plant and the only place to take the supply from is this 50A C50. due to it only being 3kA, is there a way i can get past this?
i cant just simply remove this as its in an enourmous Distribution board.
i have looked at 434.5.1 which states : -
"except where the following paragraph applies, the rated short circuit breaking capacity of each device shall be not less than the maximum prospective fault current at the point at which the device is installed.
A lower breaking capacity is permitted if another protective device or devices having the necessary rated short circuit breaking capacity is installed on the supply side. In this situation the characteristics of the devices shall be co-ordinated so that th energy let-through of these devices does not exceed that which can be withstood, without damage, by the device(s) on the load side."
The problem i am having is knowing if using an MG (Schneider) Distribution board filled with Multi9 MCB's will meet this requirement.
i have spoken to electrium and all they have advised is i see if 434.5.1 can help.
any advice would be gratefully appreciated. Thanks in advance
Peter