So been at college tonight and we covered cable calcs and diversity , something I am sure you all know alot more than me about :Salute .

Heres the figures we was given I am interested as to what you would really do.

Customer phones , wants supply to garage , with the following information what size SWA would you run to supply this;

1 A3 Radial

4 lights

1 3kw heater

Cable run of 10 mtrs 5 mtrs buried underground, through back of CU outside of building till it goes underground.

Passes through 500 mm thermal insulation.

To be protected by a BS EN 60898 MCB.

 
So a quick calc got my a design current of about 30a

That got me a 4mm 3core SWA before the insulation correction, which sedated the cable by 50%,,,, so I would have to guess at 10mm SWA (maybe?)

 
Well going by the calc as have been taught we calculated to a 25mm SWA
Wow

TLC's calculator gives 4mm, not allowing for derating. If cable just passes through insulation for a short distance do we need to derate?

 
The calc as we have been taught :

20 A Radial no diversity

4 lights at 100 W after diversity applied 1.74 A

3Kw heater no diversity 13.04 A

Design Current 35 A

In 40 A MCB

Ci of 0.51 Cc of 0.91

It = 87.14 A

---------- Post Auto-Merged at 22:08 ---------- Previous post was made at 22:03 ----------

Passing through more than 400mm of thermal insulation derates a cable by a nats over 50%

 
The calc as we have been taught :20 A Radial no diversity

4 lights at 100 W after diversity applied 1.74 A

3Kw heater no diversity 13.04 A

Design Current 35 A

In 40 A MCB

Ci of 0.51 Cc of 0.91

It = 87.14 A

---------- Post Auto-Merged at 22:08 ---------- Previous post was made at 22:03 ----------

Passing through more than 400mm of thermal insulation derates a cable by a nats over 50%
So why not 16mm - or have I missed something?

94 Amps - 16.0mm 6943X 3 core SWA Steel Armoured Cable

 
Table 4D4A pg 280 BS 7671 Current Carrying Capacity referance method D a 16mm has a rating of 78A to small

 
Table 4D4A pg 280 BS 7671 Current Carrying Capacity referance method D a 16mm has a rating of 78A to small
Not if it's XLPE - acccording to TLC ......94 Amps

As your thread says - theory against real world lol

 
I believe XLPE comes under table 4E4A 16mm is 91A so yes acceptable but would be even more costly ? and as it would be 3 core then the current carrying capacity is even further derated to 75A .

Please if I am incorrect then please correct me

 
I can honestly say if a domestic customer rang me for a quote to put some lights, sockets and a heater in their garage 5metres from their house its VERY unlikely I'd quote for a 25mm SWA 3core. Sure they wouldnt be too happy with it clipped to their external wall for the other 5 metres.

How much insulation does it pass through!? Also is unlikely radial will be pulling 20 amp's, maybe this could go on a 16amp mcb?

I would probably put it on a 4mm, 6 at most. If insulation was really that thick i'd take a different route.

Good post!

 