Just been out to look at a job,,, a few little bits and pieces to do...
But the main reason for this post is because the guy has recently had his CU replaced by a local wannabe:_| I've ot looked inside te CU yet but I have looked at the EIC
under the work covered by this certificate he has put "entire house",,, FFS all he has done is replace a CU, make a bedroom into a kitchen and the old kitchen into a bedroom!
Under PFC he's put 1502!!!! now that's a KA box,,, I think he's missed a decimal point tere somewhere??
Lighting circuits are wired in (1.0 / 0.75) and (1.0 / 0.25)
cooker circuit in (6.0 / 4.0)
Ring continuity 1.2 / 1.2 / 1.2,,,, what! And theres nothing wrong with that
I'm sure there's more,, his cert is just shocking, god knows what his work is like
:red card :red card:red card:red card:red card