Wonder if anyone can help?... Doing a pfc test on a domestic supply and getting readings of 1.88kA L-N, and 0.86kA L-E. This surely suggests it is a TN-S system?...and yet the last PIR on the property states it is a TN-C-S supply. The reason for confusion is that the main incoming cable is a lead sheath...the Main Earthing cable exits the Main Cut-Out at a MET block, so at first glance it looks like a typical TN-C-S supply...BUT, there is also an older green earthing cable leaving the bottom of the Main Cut-Out going to a clamp on the lead sheath of the Incoming cable. (NOT a BS951, but an older style clamp?)
Photo attached...I hope!
My thinking is that it USED to be a TN-S supply and was changed somehow to TN-C-S, and that cable to the lead sheath is simply acting as a Bonding..BUT...why would I be getting such a difference in the two pfc readings if it IS now a TN-C-S supply?....any thoughts out there gratefully received! :C