Thanks Sidey, that was my initial thought but the IET technical guy was more concerned as to the lightning protection system having a bearing on the bonding, he thought that the bonding would make matters worse, he was saying it would be out of the scope of bs7671 and would be subject to bsen62305?, which immediately made me doubt myself.
would the fact that all walls being metallic and each flat being bonded to the metsec cause any issues?
As I said each supply with its own MPAN needs to be completed in accordance with BS7671.
The LPS must be bonded to the earthing and bonding of the LV installation in the building.
Personally I would do this at the "master" supply, you mention shop I think, at ground level? I'd do it there.
This all needs to comply with 62305, you'll need earth rods down < 20 Ohms I think from memory, but you need to check.
There are 4 parts to 62305, £306, £318, £254, £254, in no particular order!
So that's over £1100!!!
Unless you get BSI member discount.
On top of this, if you have an LPS, you really should fit surge to all incoming lines, that's electric, phones, broadband, basically, anything conductive entering the building.
Nothing will protect against a direct strike, it's indirect strikes, and conducted emissions you are trying to mitigate against.
Look to 7671 regs below & GN8.
411.3.1.2
443.1
534.2
541.3
542.4.1(iv)
Appendix 16
GN8, Ch3, 5, & 6
EN 62305 parts 1 -4 & PD 62305 which is just the flash density map.