Evening all.
I was under the impression that in most cases, in order to meet disconnection times within a TT installation, RCD's must be used unless Ze is very low.
I have come across a 3-phase installation (caravan park) where the setup basically compromises of a panel board feeding 3x 3 phase sub boards. 1 sub board feeds a toilet block (split RCD, no RCD on lighting circuits) as well as a number of streetlights (no RCD). The other sub boards feed various caravan hookups (all with 30mA DP RCD's)
Ze=142ohms Ra=144ohms
PFC=2Ka
The 3 sub boards are fed from 160A 60947-2 MCCB's.
The circuits fed from the sub boards are protected by MCB's (type b ranging from 6A-32A)
So, I cant see how any of the distribution circuits and the circuits feeding the hookups and also the lighting circuits within the toilet blocks can meet their disconnection times?
What are the options regarding this issue, or am I completely missing something?
Cheers
GS
I was under the impression that in most cases, in order to meet disconnection times within a TT installation, RCD's must be used unless Ze is very low.
I have come across a 3-phase installation (caravan park) where the setup basically compromises of a panel board feeding 3x 3 phase sub boards. 1 sub board feeds a toilet block (split RCD, no RCD on lighting circuits) as well as a number of streetlights (no RCD). The other sub boards feed various caravan hookups (all with 30mA DP RCD's)
Ze=142ohms Ra=144ohms
PFC=2Ka
The 3 sub boards are fed from 160A 60947-2 MCCB's.
The circuits fed from the sub boards are protected by MCB's (type b ranging from 6A-32A)
So, I cant see how any of the distribution circuits and the circuits feeding the hookups and also the lighting circuits within the toilet blocks can meet their disconnection times?
What are the options regarding this issue, or am I completely missing something?
Cheers
GS