Hi All,
This might seem basic but I could use some advice.
In a domestic property the earthing arrangement is TT. A new shower circuit needs installing, but have done some testing the Ze is 74 ohms, Zs@db 4.8ohms, Ipf@db 49a
Now obviously on any new circuits to be installed, they will have a Zs value higher than the permitted value in BS7671.
My question is should I contact Western Power to have TT changed over to PME?
What needs to be done in order for a new circuit to be installed and then signed off as satisfactory in a EIC?
Many thanks for your help guys
Joey
This might seem basic but I could use some advice.
In a domestic property the earthing arrangement is TT. A new shower circuit needs installing, but have done some testing the Ze is 74 ohms, Zs@db 4.8ohms, Ipf@db 49a
Now obviously on any new circuits to be installed, they will have a Zs value higher than the permitted value in BS7671.
My question is should I contact Western Power to have TT changed over to PME?
What needs to be done in order for a new circuit to be installed and then signed off as satisfactory in a EIC?
Many thanks for your help guys