Hi all,
I am trying to sort out an installation at a farm for a friend. Yep, you guessed it, "farm" says it all!!!! I will add here, that i know that there are certain requirements for agricultural installations, but this is not one, it is a large field with horses, and horses are not an agricultural animal.....
Anyway, this place is supplied by overhead, and as the DNO have made no provision for earthing it is TT time, [or at least it should be...]
Now, over the years this place has grown and grown [and grown!] Problem is, i can find no earth rods anywhere. I asked the owner, and he alternates between; "there is no earthing" and; "i am sure there was a rod here once"!!!
All the various buildings [eight of them] are supplied by SWA cable of dubious origin, nothing is co-ordinated, and it is all a complete mess. The only provision for earthing in each building is from the cable armour, no other rods, nothing. Trouble is, there are no RCD's anywhere and Zs is 10 ohms....... not good.... Not good at all.....
10 ohms seems very good for a TT installation, but as there are no rods [or earthing conductors!!!] that i can find, i can only assume that the one large steel framed building is acting as an earth rod for the whole installation, as, like i say, it is all linked by the cable armour. Even this is by chance, as the CU in the barn is a metal one, and merely happens to be bolted to a stanchion of the building, not deliberately bonded to the steelwork or anything like that!!
Now, i installed an installation, [eh] to a new building there the other day. I used an insulated, IP rated CU, rodded it, and the new building now has its own, discrete, TT, rod and RCD setup. The owner was amazed that a proper job could be done so cheaply, and now wants the rest improving...
Now to my question...
In my opinion, having all the buildings linked together by the cable armour is a huge mistake and is dangerous. You have a TT setup yes?? Even if you DID have RCD protection, let us assume for a second that the RCD has failed. If you now have an earth fault in any ONE building, ALL exposed conductive parts in ALL the buildings, will now become live, the whole lot... Even less good.....
So, here is what i propose to do....
300mA RCD in the meter tails to protect all distribution circuits. Then, at each individual building, insulate the incoming SWA from the CU, [plastic box, insulating gland, plastic CU, whatever.] and then individually rod and 30mA RCD each building on its own. This way, at least if you have an earth fault and the RCD fails to work, the shock hazard is confined to the one building, and not transmitted to the entire complex.
What you all think????
john....
I am trying to sort out an installation at a farm for a friend. Yep, you guessed it, "farm" says it all!!!! I will add here, that i know that there are certain requirements for agricultural installations, but this is not one, it is a large field with horses, and horses are not an agricultural animal.....
Anyway, this place is supplied by overhead, and as the DNO have made no provision for earthing it is TT time, [or at least it should be...]
Now, over the years this place has grown and grown [and grown!] Problem is, i can find no earth rods anywhere. I asked the owner, and he alternates between; "there is no earthing" and; "i am sure there was a rod here once"!!!
All the various buildings [eight of them] are supplied by SWA cable of dubious origin, nothing is co-ordinated, and it is all a complete mess. The only provision for earthing in each building is from the cable armour, no other rods, nothing. Trouble is, there are no RCD's anywhere and Zs is 10 ohms....... not good.... Not good at all.....
10 ohms seems very good for a TT installation, but as there are no rods [or earthing conductors!!!] that i can find, i can only assume that the one large steel framed building is acting as an earth rod for the whole installation, as, like i say, it is all linked by the cable armour. Even this is by chance, as the CU in the barn is a metal one, and merely happens to be bolted to a stanchion of the building, not deliberately bonded to the steelwork or anything like that!!
Now, i installed an installation, [eh] to a new building there the other day. I used an insulated, IP rated CU, rodded it, and the new building now has its own, discrete, TT, rod and RCD setup. The owner was amazed that a proper job could be done so cheaply, and now wants the rest improving...
Now to my question...
In my opinion, having all the buildings linked together by the cable armour is a huge mistake and is dangerous. You have a TT setup yes?? Even if you DID have RCD protection, let us assume for a second that the RCD has failed. If you now have an earth fault in any ONE building, ALL exposed conductive parts in ALL the buildings, will now become live, the whole lot... Even less good.....
So, here is what i propose to do....
300mA RCD in the meter tails to protect all distribution circuits. Then, at each individual building, insulate the incoming SWA from the CU, [plastic box, insulating gland, plastic CU, whatever.] and then individually rod and 30mA RCD each building on its own. This way, at least if you have an earth fault and the RCD fails to work, the shock hazard is confined to the one building, and not transmitted to the entire complex.
What you all think????
john....