I've added a couple of extra sockets in today for a friend as he uses a lot of adaptors plugged into more adaptors for his tv and stereo!
Anyway Zs were only 0.68 ohms and as I have not much experience with TT systems I was astounded to get such a low reading.
I checked the Ra which came out at 291 ohms and therefore reckon that the low reading is due to the water supply pipe. This is main bonded under the sink and then the water pipes go back underground in a concrete floor before reappearing at the downstairs WC.
The earth rod is supplied by 6mm 6491x enclosed in pvc conduit but the top of the rod and connector is buried about 4-6" in the soil.
I know we shouldnt rely on the water pipes for earthing but as Zs are so low then is there any need to replace the earth rod?