I need some help boys. I've been to a job to repair under floor heating. It's never worked properly due to it being installed wrong.
It has 3x 8m mats @ 200w per metre 1.6kw = 6.9A each mat
Total = 20.7A
All 3x mats and floor stat are connected to a 13A Max time controller and has damaged the controller
Can i fit a contactor or relay somehow to fix this problem?
If so how do i do it?
Under floor heating is not my strong point!
Cheers boys