Using 1.5mm wire for external double socket

Talk Electrician Forum

Help Support Talk Electrician Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

Vedb

New member
Joined
Nov 25, 2024
Messages
4
Reaction score
1
Location
London
Hi all,

I've got a 1.5mm wire running from the consumer unit to the outside which was previously a light. I've done away with the lights and want to repurpose the wire for a couple of plug in cameras.

Appendix 15 of BS 7671:2018 says it is acceptable to use a 1.5mm cable for a socket as long as there is a fused spur first as the cable can handle up to 15 amps and the spur will limit it to 13A anyway.

However, my question is;

As this cable goes straight from the CU, with no other lights or demand, does it still need a fused spur or can it go directly without one?

Many thanks!
 
However, my question is;

As this cable goes straight from the CU, with no other lights or demand, does it still need a fused spur or can it go directly without one?

Many thanks!

Hello Vedb.. Welcome to the magical electrical forumbulator....
Even though some of us may appear strange.... Stick with it, bear-with-us, we all want to help you as best we can!!

But if you are walking around whilst waiting for replies..... remember the coffee machine on the fourth floor still only accepts the old larger sized 50p coins.. and some of the crisps in the vending machine in reception have not been re-stocked since the Covid lock-downs.. So DO-NOT choose "Cheese & Onion" or "Smokey Bacon" unless you like soft crisps!!!!

Meanwhile.....

All cable connections into modern consumer units will terminate into an MCB / RCBO..
(The replacement of the old fashioned fuse-wire holders).

They will all have a maximum current ratings, (e.g. 6A, 10A, 16A, 20A, 32A etc..), before they disconnecting the supply to prevent the cable being damaged in the event of a fault.

So first you need to find out what is the current rating of the MCB /RCBO in your CU that supplies this cable?

You didn't say if this 1.5mm cable is a PVC, (T&E), or SWA? As a SWA with the same sized conductors can generally carry a bit more current than T&E PVC..

As a rough rule-of-thumb depending upon installation methods 1.5mm T&E can be limited to 10A or 16A max..
Where as 1.5mm SWA is often good up to 20A!

However back to your question... If you just want to power a couple of cameras..
I'd probably just put the 1.5mm onto a 10A MCB/RCBO in the CU, and connect it to however many sockets you need..
As the 10A should be good for the cameras, and the cable will be protected no mater how it has been installed!
 
Many thanks for your replies all, appreciated. I will check the CU today as I've been away from site and revert with a photo 👍🏻
 