New to the Inspecting part, and the testing.
This is linked to my other thread (rented property)
Called round today for a proper look at what was going off, any how doing a visual report for them just so they are aware of what is what.
Im in need of a hand coding the folllowing please.
1. Gas Meter is only 3" from the Main Fuse (it runs across the front of the fuse)
2. 10mm Tails into the CU from Henley Blocks after meter
3. Shower is on 10mm via a old "shower unit" with a 32amp MCB, which fair enough. but the cables when terminated, due to not been able to fit the 10mm into the connections, they cut some of the strands off the cable and bent them around.
4. Earthing. 4mm Main earth on a the sheath of the incomer upto the CU, but then there is another 4mm, which goes into a Connector Block which disappears next door along with main supply for the next door.
See my crappy drawing
5. No earth to metallic fronts (earth is just snipped off)
6. Socket directly above HOB
7. Cooker Hood Switch (used a 3 way isolator, used in bathrooms) and links neutral) just switched live. Earth is Cut. The supply is picked up direct from the socket below, Again Switch is directly above the cooker hob. (Hob is Gas)
8. No earth to stop Tap
9. No cooker isolation for electric oven, wired direct into ring main.
10. No labelling/sleeving with colours in switch's for the switch live.
11.No Bonding in Bathroom
12. No RCD protection to any location (downstairs sockets can be used for items suck as electric gardening tools)
Just need a hand with the codes if possible.
thanks in advance
This is linked to my other thread (rented property)
Called round today for a proper look at what was going off, any how doing a visual report for them just so they are aware of what is what.
Im in need of a hand coding the folllowing please.
1. Gas Meter is only 3" from the Main Fuse (it runs across the front of the fuse)
2. 10mm Tails into the CU from Henley Blocks after meter
3. Shower is on 10mm via a old "shower unit" with a 32amp MCB, which fair enough. but the cables when terminated, due to not been able to fit the 10mm into the connections, they cut some of the strands off the cable and bent them around.
4. Earthing. 4mm Main earth on a the sheath of the incomer upto the CU, but then there is another 4mm, which goes into a Connector Block which disappears next door along with main supply for the next door.
See my crappy drawing
5. No earth to metallic fronts (earth is just snipped off)
6. Socket directly above HOB
7. Cooker Hood Switch (used a 3 way isolator, used in bathrooms) and links neutral) just switched live. Earth is Cut. The supply is picked up direct from the socket below, Again Switch is directly above the cooker hob. (Hob is Gas)
8. No earth to stop Tap
9. No cooker isolation for electric oven, wired direct into ring main.
10. No labelling/sleeving with colours in switch's for the switch live.
11.No Bonding in Bathroom
12. No RCD protection to any location (downstairs sockets can be used for items suck as electric gardening tools)
Just need a hand with the codes if possible.
thanks in advance