Dead link. this seems to be happening a lot lately. If anyone else can see the link, please re post it. Otherwise can you try again Lee?
He said,
I can see the link. Is this any help Dave?Dead link. this seems to be happening a lot lately. If anyone else can see the link, please re post it. Otherwise can you try again Lee?
I can see that one, but not the one in the post above. I get "Invalid Attachment specified. If you followed a valid link, please notify the administrator" this happens quite a lot, that some can see an attachment, while others can't. Strange.
#16.....Have any of these 'voltages' actually been measured with reference to incoming earth..i.e. wander lead to the sink and dishwasher....
For example...
Could be sink @ 0v and D/W @ 60v
or
sink @ 60v and D/W @ 0v
or
Sink @ 30v and D/W @ 30v
Would all give the same apparent fault potential between the two devices...
But need to know exactly whats what...
Remember there is NO specific requirement to supplementary bond sinks or draining boards...
top of Page 43 on-site-guide
You could be introducing a potential difference that wasn't there by bonding. :C
Now... where does it say you need to maintain bonding continuity to a kitchen sink? :C
Indeed!....Thought that kitchen sinks need no bonding providing the rest of the installation complies with current regs. Await incoming.
This makes sense, i havent heard of a constant force spring, but the owner did mention the engineer said something about a "spring" thought she heard it wrong. Cheers.This bit of your post lends me to think that they have a TNS supply. It sounds like he's fitted a constant force spring around the service sheath.A PME or TNC-S (which are not the same thing BTW) earth would be connected within the service head.
Im guessing that its going to be alright now, im hopeing its fixed the issue, maybe the earth path wasent good enough before.I can see that one, but not the one in the post above. I get "Invalid Attachment specified. If you followed a valid link, please notify the administrator" this happens quite a lot, that some can see an attachment, while others can't. Strange.Anyway, that's not what I know of as a TNCS head, and there's no connection the the sheath. Looks like the DNO fitted the missing earth connection when they visited so hopefully that's the end of the floating earth issue.
In my previous post, i mentioned i didnt carry out a Ze test, because i was not certain on what conductor was the earthing conductor.Well I would still be interested to hear any answers from my post #9..... :C Or post #16?????
Wouldn't a Ze / (Ra) test at the CU have confirmed if there was an earth path....
rather than getting the DNO out???
COPY post#9:-
#16.....
Who indeed??Thats where im at now.(who cares?)
Hi Noz,Lee,It always was a TN-S from what I could tell from your photo, although I personally dislike perforated strap screwed underneath a MET as I've found that they become loose.
Did you check the RCD with the loads disconnected? Otherwise your tests are pretty meaningless I'm afraid
I can't remember if you've done a long lead from the MET to the sink and dishwasher,, if you haven't then I would check for continuity and voltage.
It might also help if you could connect an auto-ranging (with peak hold function) betweeen the dishwasher and sink for at least a full cycle.
Hi Kme,Lee:If a test fails, don`t blindly carry on to the next one.
If the RCD didn`t trip at 1X; why test it at 5X? un-necessary risk.
You say your meter occasionally trips RCD on Ze test? Now I find that really scary, COS IT SHOULDN`T BE ENERGISED TO START WITH!
"You started"; but I`m not sure you can finish.
Who indeed??
Your college taught you wrong then!Hi Noz,I tested the RCD with loads connected. We was taught at college to run a RCD test with the installation engergized, either a kettle lead from meter in a socket outlet or a 2 or 3 lead instrument at a lighting rose etc, so im not with you there?
Lee, you misunderstand. My post was intended as guidance, not to belittle you or anyone else. If someone is out of their depth for whatever reason (some people can`t get their heads around 3phase; others can struggle with some aspects of fault finding), then I think it best to point out that they may be unable to resolve the problem, due to either a lack of understanding of the procedures required, or simply a lack of experience in these types of fault.Hi Kme,
I came on the forum to basicaly ask for a little guidance, not to be be-littled.
Mate - if a topic is of no interest to me, or I don`t believe I can offer anything useful - I don`t respond at all. I was attempting to provide my opinion, based on the info. you`ve provided within this thread. Maybe I shouldn`t have.Heck, someone else, who is learning of course(none of us are born with all the experiance and knowledge)might learn something for the topic.
Sorry if the topic was of no interest to you.
I`m not about to "fall out" with anyone - and I don`t consider my response to be out of character with my typical responses to similar scenarios. Sorry if you didn`t like it. :CBlimey, i dont want to fall out with anybody on these forums, but did someone poo in your cornflakes yestoday?
Thats good news, as it goes to show we have real human members, not robots, and the forum is still encouraging debate. Heres another observation. With over 18,000 members, over 600 persons on-line at this point in time, An experience spectrum from DIY though to 30+ year time served, 3-phase heavy industry to domestic to camping sites etc. I am not surprised that there are occasions when one member or another may find a question rather basic. As it has often been said, the written word on a forum does not display body language or tone of voice very well. Some people occasionally dislike the way they are told some thing, this is common place throughout workplaces and homes around the country. Debate and discussion typically has opposing views, (listen to the average banter in the typical pubs and clubs in the towns where you live). The forum is part of this real world and there will be differences of opinion, any person expecting everything to be all yes sir and full agreement has unrealistic expectations. However, where there are opposing opinions, it will not resort to bad language and a basic level of respect will be maintained, otherwise members will not be welcome to discuss the various topics.Seems quite a few people feel "belittled" after posting questions lately. Just an observation.