Hi All,
Replacing two class 1 wall lights (lights only, not the circuit) for a customer.
They've been wired off the ring final via a switched fused spur.
It's a TN-C-S with final circuits protected by BS 3036s.
My question is this:
When measuring my Zs from the lighting points, do I compare it to the OSG figure for a 30A 3036 (which is 0.9, pg100) or do you take into account that the lighting spur is protected by a 5A 1362.
I haven't measured it yet, but I am just a bit worried that the 0.9 might not be achievable.
Thanks for your help.