I was at a job today (PIR/fault finding) it's a TT installation and the tails go into a kmf switch fuse and from there 16mm T&E in through the wall, up the inside (burried direct), through the loft (clipped to a purlin) and then down behind the plaster to the CU. The CU is a dual 30mA RCD board (Volex,,, pah)and they've put the main switch right in the middle:O very odd configuration IMHO!
Now the problem is that the incomming sub main has no RCD protection, it's a TT installation and the cable is burried <50mm. Realistically the cable needs 30mA protection, but I can't do that due to discrimination.
Is my only option to replace the T&E with SWA and give it a 100mA TD RCD at source? Or is there another way?
Now the problem is that the incomming sub main has no RCD protection, it's a TT installation and the cable is burried <50mm. Realistically the cable needs 30mA protection, but I can't do that due to discrimination.
Is my only option to replace the T&E with SWA and give it a 100mA TD RCD at source? Or is there another way?