about? As Green Hornet said, contact DNO.to be honest I'm stumped 10ohm difference ...but on a tn c s all controlled by the DNO so go on give us a clue ?????
about? As Green Hornet said, contact DNO.to be honest I'm stumped 10ohm difference ...but on a tn c s all controlled by the DNO so go on give us a clue ?????
can you verify the safety of the installation?Does that mean Im right Mr Steptoe ? ?:|
About the correct answer for this question.....Guiness Drinkabout? As Green Hornet said, contact DNO.
if an earth is provided, it must be maintained.sorry GH, but I think that is wrong,that is what all the calcs given in 7671 are based on,
but I think its down to the DNO to verify what they will actually give you.
I have found that in most cases they will simply disconnect and tell you they are no longer supplying the earth if it is too high.
this is the very reason i come on here the advise is excellent. you dont learn this stuff on site.. keep up the good work guys..One of the first things I do when quoting for a rewire is a Ze test, this I do on the first visit.I did a rewire last year on a very large house, the house next door had had a rewire a year earlier.
When I tested the pme I found a Ze of 0.57, I asked if I could test the next door and found they had a reading of 0.58.
The electrical installation cert for that property had a reading of 0.35 for the actual reading of Ze.
I contacted the dno, who came out twice to survey the problem, eventually they sent a field team out and found a fault on one of the overhead cables.
After the fault had been rectified the Ze readings on both houses droped to 0.12
Another case I had was a pme reading of 0.39 slightly over the max permitted of 0.35,
again I contacted the dno who said they would monitor the situation but would not take any further action at this time.
I noted the deviation on my EIC with a note detailing the conversation I had with the dno.
If a repair can not be made the dno will disconnect the tail from nuetral and remove there obligation to supply an earth leaving the electrician liable to install the correct earthing requirements.
Its better to find out before you start a rewire than after.
I do like to hear that members find the advice on the forum to be good. Not sure taking your technical books on holidays is required though, maybe a bit of lighter reading more appropriate JL?this is the very reason i come on here the advise is excellent. you dont learn this stuff on site.. keep up the good work guys..the wife just says that i am sad, i just packed my onsite guide and some other stuff to read while on holiday lol....
I think there are many "lowly DI's" on the forum, who's input is very valuable and listened to by others. Your input is also important Dan.but ive already stated that the house is piped in copper . Yet it still wasnt bonded. Ah balls to it i give up. You experienced sparks obviously aint gonna listen to a lowly DI.
ok folks, Im getting a little mixed up now, so I apologise in advance as to if I have it wrong.if an earth is provided, it must be maintained. But if it is a DIY PME, when it should be TT, then they could disconnect and leave it TT
dans words not mine,i know the regs are for guidence and own judgement should be used in some installtions but i ive seen sparks doin some real dodgy stuff.no bonding on lead mains water and gas pipes in an old terrance with copper throughout is askin for trouble in my book.im not tryin to start an argument just pointing out that there are bad sparks which ever route they took to become one.
simply changing it from TN to TT isnt always an option. Incase of high reading on TNS or PME, then its usually a joint on their underground network thats failed. it will effect other properties and possible for the joint to completely fail, so will need rectified.Equipment on a consumer's premises24. - (1) A distributor or meter operator shall ensure that each item of his equipment which is on a consumer's premises but which is not under the control of the consumer (whether forming part of the consumer's installation or not) is -
(a) suitable for its purpose;
(B) installed and, so far as is reasonably practicable, maintained so as to prevent danger ; and
© protected by a suitable fusible cut-out or circuit breaker which is situated as close as is reasonably practicable to the supply terminals.
ha ha,From ESQCRsimply changing it from TN to TT isnt always an option. Incase of high reading on TNS or PME, then its usually a joint on their underground network thats failed. it will effect other properties and possible for the joint to completely fail, so will need rectified.
they cant exactly go round and knock on a few doors and say 'we have a probTTlem with out wiring, you will need to call a spark and get him to change your earthing to '
full text of ESQCR is here
they are obliged to give PME for new supplies (reg 24- (4))ha ha,yes I get your point, apologises,(thats not spelt right)
but perhaps at same time its also a case of they are not obliged either?
it does seem a grey area.
thanks for the info mind. good to know.
by the way, I have no idea how I moved the into the middle of probTTlem so I cant move it back.!
Not on farm installs or caravan parks and a few others.they are obliged to give PME for new supplies (reg 24- (4))for existing, if they have provided it at some point in the past, it must have been safe, and so should be maintained at all times
and for the moving on TT, if you click to edit your post, you can alter the text in my quote, like i did in your quote there
but if they are so far away from Tx that loop is over 0.35, then your probably gonna have problems with VD, and possibly Zs (and maybe even phase/neutral loop so dead short wont trip breaker in time)surely with pme or any other system it will depend how near you are to the transformer as to what loop you get. Sometimes they may not be able to give you a pme supply if loop is over .35ohms. I understand about bad joints but that may not be why loop is so high.Batty
it saysNot on farm installs or caravan parks and a few others.
but it also says elsewhere that PME cannot be used in certain conditions (like the caravans you mentioned), but incoming supply to site can be PME and so can certain buildings(4) Unless he can reasonably conclude that it is inappropriate for reasons of safety, a distributor shall, when providing a new connection at low voltage, make available his supply neutral conductor or, if appropriate, the protective conductor of his network for connection to the protective conductor of the consumer's installation.
that shouldnt be an issue, after all on TNS its 0.8,but if they are so far away from Tx that loop is over 0.35, then your probably gonna have problems with VD, and possibly Zs (and maybe even phase/neutral loop so dead short wont trip breaker in time)