So bell out the pairs I.e U1-U2, V1-V2 and W1-W2 and make them off in pairs into the DOL 3 phase starter/terminals?Canoeboy said:7 core - so 6 cores (3 for U1,V1,W1 and 3 for U2, V2, W2) and 1 core for earth presumably ?
Yes you can wire the 6 cores to a 3 wire DOL (either 3 wire delta or 3 wire star depending on the voltages)
It will be in delta I believe. Cables numbered 1-7. So I can't just bell them out? this will get messy.Canoeboy said:Not as simple as that, and if the 1's and 2's are not marked you'll be stuffed. And they may be marked up X,Y,Z or A,B,C etc U1 and V2 etc was an example.
It also depends if you need to run the motor in star or delta (probably delta - but without seeing the motor/nameplate its hard to be 100% correct)
So assuming the 1,2,3 are 1s and 4,5,6 are the 2s would they then need to be paired and made off? i.e 1 & 4 together in a terminal and 2 & 5 together and so on?You can bell them out to find out which pair goes to which winding and label them anyway you like, e.g. for windings U, V & W.
However, you will then need to find which is the start and end of the winding, i.e. the 1 & 2 that Canoeboy refers to.
You will be able to see that two windings have the same volt drop and the third is different
Actually had time to read the above now!! Would not fancy connecting up 240V in the way described.... Cannot see the winding being very pleased at all... Maybe a daft idea...
Still, there we are!!
john..
We just use a 12 volt battery across one winding whilst there's an analogue DC ammeter that can measure low miliamps connected to another. You adjust the zero point of the needle using the calibration screw on the front of the meter so the needle sits somewhere above the zero then tap the winding wires momentarily onto the battery and note which way the needle makes a small deflection. Repeat with other windings and reverse them accordingly until the meter deflects the same direction regardless which winding the meter and battery are on.
It's an interesting thought. It's something I've never seen done that way but in theory it could work with an LED although some may be more suitable than others due to forward volt drop requirements. I was shown this method durng my apprenticeship at which time it was much easier to lay your hands on an analogue galvanometer than an LED. Maybe give it a try and let us know.Am i right in thinking this is also achievable with an LED if you don't have an analogue meter?