Went fault finding today on a RFC.
Apparently, the MCB has been tripping intermittently.
It's a split load (single RCCB) - lights and a socket radial (one double) on the RCD side..............RFC, Shower, boiler on the other side.
That should have made me suspicious straight away.
Anyway, isolated whole board and completely removed the two legs of the ring from the CU.
Simple things first - end to end continuity...........there was continuity, but measurements were in the Kohms range - not good.
IR tested.....L-CPC, L-N, N-CPC..... all bad - 0.02 Mohms or there abouts.......N-CPC being the worst.
To cut a long story short, I removed socket fronts, continuity to find which socket fed which etc. and IR tested each section of cable.
Discovered there is at least one JB hidden somewhere and that there was a spur feeding two double sockets.
Also discovered there was a bad section of cable between two sockets.
Thought best solution would be to remove bad cable from circuit and form two 20A radials.
It was getting a bit dull now, so I re-energised the board so I could use the lights.
I formed the two radials and replaced the socket covers and headed back to the CU for the tests.
IR test radial one -
>299 Mohms N-CPC, L-CPC, L-N
IR test radial two -
N-CPC >299
L-CPC.............meter starts beeping and registering 230V between Line and CPC??????
I couldn't believe it, so I double checked with my Martindale.....it was true.
I'd just replated all the sockets with 230V on the 'Line' conductor.....felt a bit ill.
Knowing the voltage had to come from somewhere, I started opening the MCBs..........turns out to be the shower??
I asked the customer and he insists that the 6mm feeding the shower is one continuous run from board to shower(via isolator), but I wonder!!
I wanted to post this as a little reminder that you just never know when or how something might be 'live'.
I also wondered if anyone had any ideas..........I'm back there tomorrow to carry on.
I guess we don't have to wonder why the original spark put the sockets on the non-RCD side of the board. X(
Apparently, the MCB has been tripping intermittently.
It's a split load (single RCCB) - lights and a socket radial (one double) on the RCD side..............RFC, Shower, boiler on the other side.
That should have made me suspicious straight away.
Anyway, isolated whole board and completely removed the two legs of the ring from the CU.
Simple things first - end to end continuity...........there was continuity, but measurements were in the Kohms range - not good.
IR tested.....L-CPC, L-N, N-CPC..... all bad - 0.02 Mohms or there abouts.......N-CPC being the worst.
To cut a long story short, I removed socket fronts, continuity to find which socket fed which etc. and IR tested each section of cable.
Discovered there is at least one JB hidden somewhere and that there was a spur feeding two double sockets.
Also discovered there was a bad section of cable between two sockets.
Thought best solution would be to remove bad cable from circuit and form two 20A radials.
It was getting a bit dull now, so I re-energised the board so I could use the lights.
I formed the two radials and replaced the socket covers and headed back to the CU for the tests.
IR test radial one -
>299 Mohms N-CPC, L-CPC, L-N
IR test radial two -
N-CPC >299
L-CPC.............meter starts beeping and registering 230V between Line and CPC??????
I couldn't believe it, so I double checked with my Martindale.....it was true.
I'd just replated all the sockets with 230V on the 'Line' conductor.....felt a bit ill.
Knowing the voltage had to come from somewhere, I started opening the MCBs..........turns out to be the shower??
I asked the customer and he insists that the 6mm feeding the shower is one continuous run from board to shower(via isolator), but I wonder!!
I wanted to post this as a little reminder that you just never know when or how something might be 'live'.
I also wondered if anyone had any ideas..........I'm back there tomorrow to carry on.
I guess we don't have to wonder why the original spark put the sockets on the non-RCD side of the board. X(