ZE in a factory

Talk Electrician Forum

Help Support Talk Electrician Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

manutd4life

Junior Member
Joined
Sep 4, 2012
Messages
28
Reaction score
0
Hi all

Ive added a circuit on a warehouse thats supplying an outside cabin,  now ive tested the cable ive installed but i have no access to the incoming supply and no test sheets are available for me to get the ZE reading and can't see what the earthing arrangement is.  What options do I have? 

Thanks

 
Not verified.

As long as your test results are fine you can only do so much.
What do I write on the test sheet? Obv the 1st sheet with supply details will be pretty much blank. No incoming sizes, what phase, how many poles etc. 

 
What do I write on the test sheet? Obv the 1st sheet with supply details will be pretty much blank. No incoming sizes, what phase, how many poles etc. 


I would say you need to be VERY specific about what you write as the scope of works and the limitations of testing. You can only write what you did and why.

Your key tests are Zdb, R1 + R2 and Zs along with the IR, and RCD (if relevent)

 
Well I persisted with getting information from the job. Went back today and finally got hold of an indate EICR with the supply details on. Happy days. 

Thanks for the suggestions and help. 

 
Well I persisted with getting information from the job. Went back today and finally got hold of an indate EICR with the supply details on. Happy days. 

Thanks for the suggestions and help. 


Strictly speaking it could be argued that reg 132.16 requires you to establish the type & integrity of the supply characteristics (e.g. earthing arrangements)..

BEFORE you do any alterations.. {temp or permanent}

Guinness       

 