Hi everyone, I am new to the forum and to the world of electrical installations. I completed my domestic electrical training back in August and so far have not gone for scheme membership as I am a stickler for making sure I get things right before committing to working on a customers installation. Sorry, am rambling. I'll get to the point.
I am doing various tests on my own installation and I got a slightly high Ze measurement (.39) TNCS. At the time I took the measurenent at the main switch in the CU. Although the current at this measurement would be enough to clear the service fuse (60A BS1361) in .4 seconds, I was left wondering if I should have measured at the RCD main switch which is on the meter tails before the CU? I have just done the test at that point and got 0.17 ohms, which is a vast improvement, I also retested at the CU main switch and got 0.34 ohms which is also better than the other day. The overall point is, where is the correct position to take the reading?
I look forward to your comments. Thank you.
I am doing various tests on my own installation and I got a slightly high Ze measurement (.39) TNCS. At the time I took the measurenent at the main switch in the CU. Although the current at this measurement would be enough to clear the service fuse (60A BS1361) in .4 seconds, I was left wondering if I should have measured at the RCD main switch which is on the meter tails before the CU? I have just done the test at that point and got 0.17 ohms, which is a vast improvement, I also retested at the CU main switch and got 0.34 ohms which is also better than the other day. The overall point is, where is the correct position to take the reading?