Also another reason someone may not do zs.
They are just lazy f****rs, or don't know what they are doing.
It's the easiest test and possiblly one of the most important, as others have said, it confirms what you have already measured.
Since when did this turn into the SF Forum! Abuse without justification is frankly rather pathetic! Grow up, Cut the superior attitude and fall in line with the rather civilised and informative posts that we normally have!
1) Fully accept that in inspection and testing dead tests must precede live tests. I don't believe this is what is being advocated by many of the posts.
2) I cannot envisage a situation where a low voltage R1 + R2 resistance reading will be lower than a Zs - Ze reading. Quite the reverse. Can anyone state an electrical reason why they think otherwise!
3) Ceiling 10ft up - chandelier fitted by DIY Joe to a lath and plaster ceiling by choc blocks and insulation tape to a system without an earth - I hope you did an R2 or R1 + R2 check before you started a Zs!
4) There is nothing actually wrong with doing a Ze + R1 + R2 reading otherwise it wouldn't be an accepted test technique.
5) I've been looking at this from a PIR point of view. Assuming that mostly lights are pendants and in good condition - no real problem with a Zs. Agree - easy. However so many places with tacky metalic fittings! My compromise is to do R1+R2 at the logical end of the circuit (how do you really know?) and to check R2 at all other points where there are metalic fittings. This to my mind is a compromise that I'm happy with - though obviusly it's not perfect. Can anyoone think of anything better?
6) When having to take a light fitting off to test it - how do you know you haven't introduced a fault when you replace it?
7) Reckon I'll be getting some of those lighting adaptors. Sounds like a good way forward, as no dismantling of the fitting!
This is a forum where we ought to be getting to the heart of electrical matters, learning and agreeing good techniques. Can we please cut the c**p!
(Sorry guys - I've been decorating before the carpet fitter comes on Thursday - and I hate painting! More tolerant mood will be resumed tomorrow (or if the paint job's rubbish - Thursday!)