Wylex split load board, installed 2 weeks ago
Field called me on a Sunday afternoon saying 1 side tripped and now he's resett it but test button dosn't work.
So I grab a spare rcd a few tools the wife and kids as they very mad about helping a good friend.
Test rcd button and times. Button dosn't work and 1x above 310ms.
So swap rcd to another and same results.
When you plug something in on socket circuit it trips rcd now, he says wasn't before.
Insulation at 250v live neutral + e above 200
My wife going mental so agree with mate I'll go back on Monday
Coincidence both rcd faulty or am I missing something.
Am I been thick over looking something simple