  1. Steve3948

    3 Phase Motor 2.5mm 30A Mcb

    Yes, I'm now thinking I may be wrong having thought about it, but for some reason I felt I had come across this in the past, still felt Code 3 more appropriate though. I gather it's a small hydraulic single lift installed some 20 years ago, 3 phase  motor, wired with 2.5mm SWA to a 30A Mcb.
  2. Steve3948

    3 Phase Motor 2.5mm 30A Mcb

    So today had a call from another contractor asking if a 3 Phase Lift Motor wired in 2.5mm on a 30A Mcb was a Code 2. Cable undersized for fuse rating, should be 20A or cable size increased. Now I replied it's ok from memory, having dealt with this before many moons ago, as across 2 phases 400V...
  3. Steve3948

    New Laptop

    Acronis I'm sure claim that with their backup program you can clone to another device, not sure how or if I dreamed It could :-)
  4. Steve3948

    50V On Garage Earth

    As one of the older Electricians on this forum, what is it about the younger ones that they feel they must argue or disagree about every detail when someone posts and then with each other. I still find things I did'nt know after 44 years is this trade. If I don't know something I welcome the...
  5. Steve3948

    Which Consumer Unit?

    Less than £58 at WF
  6. Steve3948

    Smoke Detectors

    But that standard was set before Detectors with 5 Year batteries were a available. It's technology and moving with times, when something comes along then the standards should move with times and say mains operated or 5 year battery minimum.
  7. Steve3948

    Smoke Detectors

    If they should be replaced every 5 years regardless, and you can now buy them with 5 year built in batteries, why should they have to have mains supply. Is just head in the sand stuff. Apparently some LBC accept this.
  8. Steve3948

    Niceic Brcs Website

    Doubt it seeing as it was down at 1:00pm on Saturday. However back up now, but now I have catchup which I could do without on a Monday.
  9. Steve3948

    Do Not Switch Off

    My thoughts were surely the label should be suffice and I had assumed for the best part of my life that these were "Lock Off Kits" and not "Lock on Kits" Whats stopping someone applying locks to both devices thinking they are doing right. I don't believe "Locked On" can be acceptable  in any...
  10. Steve3948

    More Problems With Vlc Media Player...again.

    Disable Nortons for 15 minutes and see if its any better.
  11. Steve3948

    Do Not Switch Off

    Hmmmmmm
  12. Steve3948

    Niceic Brcs Website

    Should be back up by 10:30pm tonight, but I'm not bothering then. I contacted Domainmonsters.com, who replied saying they were in contact with the owners. If the are going to market the use of online services they must offer 24Hr support, we don't all have weekends off.
  13. Steve3948

    Niceic Brcs Website

    Still down today  :yawn Saying not a secure connection.
  14. Steve3948

    How Many People Test L-N Loop With Rcbo's?

    Amtech and NICEIC certificate software input max ZS limitation once you enter the RCD details, so maybe that's why.
  15. Steve3948

    Why Can't We Put 4Kwp On Every House?

    I'm not moaning anout the state of the country, for me its never been better, perhaps I'm one of the richer getting richer