I have carried out an EICR in an installation with multiple DBs and many RCBO devices for ring circuits. The copy of the original installation cert listed max Zs as 1666 Ohms (30ma trip). The RCBOs were mainly C type 32A. After testing ring continuity on several circuits it became apparent that a significant number of the circuits were far too long, 2.5/1.5 T/E L-L 1.65 Ohms, E-E 2.8 Ohms for example.
The earth loop reading 1.25 Ohms exceeds the max Zs for a C type thermal/mag trip (now 0.68 Ohms) but is well within RCD limit so should be OK, however if you look at L-N loop reading 0.93 Ohms which does NOT have RCD protection, the disconnection time for thermal/mag trip is not met.
My question is how many people on here would test L-N loop on an RCBO in these circumstances?
A quick straw poll of peers had interesting results!
The earth loop reading 1.25 Ohms exceeds the max Zs for a C type thermal/mag trip (now 0.68 Ohms) but is well within RCD limit so should be OK, however if you look at L-N loop reading 0.93 Ohms which does NOT have RCD protection, the disconnection time for thermal/mag trip is not met.
My question is how many people on here would test L-N loop on an RCBO in these circumstances?
A quick straw poll of peers had interesting results!