play nicely now @Murdochand attitude like yours borders on arrogance and the intent to rip people off
play nicely now @Murdochand attitude like yours borders on arrogance and the intent to rip people off
i amplay nicely now @Murdoch
But BS7671 is only a guide itself.The Guides are not official documents to cite the correct Code to quote. BS7671 which I work to only suggests Coding for one departure and experience allows me to correctly Code other departures as necessary. Guides can lead to blindness as opposed to competence and engineering judgement.
The Guides are not official documents to cite the correct Code to quote. BS7671 which I work to only suggests Coding for one departure and experience allows me to correctly Code other departures as necessary. Guides can lead to blindness as opposed to competence and engineering judgement.
i stick up for Joe Public so they can see that numerous people in our trade can feel they can trust us. Too many sharks taking the mickey and yes the BPG isn’t an official document and at the risk of repeating myself is the only document that the public can turn to for guidance and as the NICEIC state their contractors should use this as there point of reference I for once agree with them
seems my friend doesn’t agree, but fails to offer anywhere the public can seek guidance
My mother in law commissioned and reort through their letting agent for a flat they own in Chelsea. Came back with a few C2's, FI's and the usual C3's.
High Zs on some circuits yet R1+R2 and Ze are good. Low IR on some circuits from a global test but they couldn't gt in to isolate the boiler so I suspect this has dragged them down. No RCD protection for cables buried in a wall, even though it's run in Galv conduit. No RCD protection for circuits in bathroom but no mention of supplementary bonding, Easy to swap MCB for an RCBO if needed.
30 odd downlights not fire rated with dwelling above. However I've yet to find out if they're needed as I suspect the building is concrete construction and may already be dedicated fire compartments.
The remedials quote was £4700.
A counter quote from another company through the agents is £2700.
I quoted them £1700 and that wan't family rate, I actually added more as I don't want the work and I don't like her.
I quoted them £1700 and that wan't family rate, I actually added more as I don't want the work and I don't like her.
and the intent to rip people off
Tester 1 (NAPIT) was the first and last EICR with a SATISFACTORY result. Tester 2 (NICEIC) was a new company who is rogue in my opinion and Tester 3 (NICEIC) is another company.glad you didn’t stick with tester 1 now
Which circuit L,N or E(CPC) or do you mean all 3 circuits?.
Circuit 3: Max Zs Permitted = 1.10, Measured Zs L=0.16, N=0.16, CPC=0.29.
The upstairs sockets continuity results are different when they should be the same.
View attachment 11467
If I commissioned another company to do an EICR. Would tester 4 results be the same. Dare I say it. Could tester 3 loosen the downstairs socket wires to obtain the his results?I would say Tester 3 readings are totally wrong considering you have two sets of previous results to compare it with.
unless it’s 2.5 / 1 mmabsolutely garbage, we expext the CPC to be 1.67 times more than L , so ever so slightly high, but that could easily be a slightly poor contact on the test probes.
Yes, the 3rd inspector received the full report of both previous EICR's with the company names redacted.did you provide a copy of an EICR to the 3rd inspector?
Scary thought.....Did they ever make 2.5mm T&E to that spec?unless it’s 2.5 / 1 mm