Hi,
Sorted out a fault today on a tt system earth fault on the rfc. The consumer unit was metal clad & the front end rcd was 100ma. The tails had been split via a 100a main switch within an enclosure to a second consumer this was plastic & contained a 30ma rcd feeding an outdoor supply to the shed. I have told the customer that the metal clad ccu unit should be changed and also all circuits should be protected by 30ma rcd as it is a tt system.
My question is where they have split the tails with a 100a main switch could i change this with a 30ma rcd and leave the metal clad in. The customer is 92 years old. To me it seems the simplest solution but i'm not sure.
Question 2. What coding would you give on EICR for metal clad ccu, and for having a 100ma rcd rather than 30ma on a tt as i would have thought C1 or C2 but the electrician i was with said C3
Cheers
Sorted out a fault today on a tt system earth fault on the rfc. The consumer unit was metal clad & the front end rcd was 100ma. The tails had been split via a 100a main switch within an enclosure to a second consumer this was plastic & contained a 30ma rcd feeding an outdoor supply to the shed. I have told the customer that the metal clad ccu unit should be changed and also all circuits should be protected by 30ma rcd as it is a tt system.