Because the resistance per meter values of the conductors are given at an assumed temperature of 20

 
I'm not aware that Appendix 4 contains resistance per meter figures?

 
I'm not aware that Appendix 4 contains resistance per meter figures?
The resistance figures in appendix 4 are based in an operating temp of 70 C spin, so no need to apply a factor.

 
What resistance figures in Appendix 4?

Could you give a page number?

 
Those figures are not resistance per meter.

They are current carrying capacity and voltage drop figures.

 
Never even considered looking at those.

Was taught to use the Tables in GN3 for some reason.

 
I agree that you may have been mislead, you apply the 0.8 or 1.2 factors when calculating R1+R2 values, not on the current carrying capacity

 
Top