17th cable sizes

Help Support Talk Electrician Forum:

copdog

Junior Member
Joined
Jul 14, 2008
Messages
9
Reaction score
0
What do you peeps think about the derating of t&e in thermal insulation in the 17th ? , my niceic area guy told me that it will have to be 4mm rings for 32a 0r 4mm 20a radials for power and 10mm run in conduit for showers over 40a. What joy !!

 

SPECIAL LOCATION

Trailer Boy - Electrician.
Joined
Mar 28, 2008
Messages
13,633
Reaction score
317
What do you peeps think about the derating of t&e in thermal insulation in the 17th ? , my niceic area guy told me that it will have to be 4mm rings for 32a 0r 4mm 20a radials for power and 10mm run in conduit for showers over 40a. What joy !!
OR..

ensure the cables are not completely covered by thermal insulation..

and/or clipped so as touching an inner wall/joist surface..

Table 4A2 gives four installation methods, 100,101,102 & 103 re flat T&E PVC,

the worst option being just "chuck it in" leaving it buried on all sides in insulation..? not clipped to any inner surface!

Me thinks need to create a bit more air space around cables..

e.g. the conduit option discussed above??? and a little more thought on cable routes and fixing method required... ?:| ? :|

 

sirsparkabit

Well-known member
Joined
Mar 19, 2008
Messages
437
Reaction score
14
Specs i always clip my lighting cables in lofts so they are touching the joists on one side. :D

after all what else can you do!. ; \

When you take the price of copper into consideration and the lack of resorces this would clearly show the 17th to be very unenviromentally friendly. X(

i dont think we should be increasing cable sizes if not warranted. ]:)

 