never the less they fit them and ask us to so we do .
JL - can you name me 1 reason to fit a 100mA when everything is protected by a 30mA?there are reasons to fit and reasons not to bother i would rather aire on caution and over protect. i only know we fit them and sometimes its a pain to actually sourse 1 but there you go we sleep at night knowing all bases are covered.
and im telling you not to, so dont (but still charge the same price)kieth says fit 1 so we do,
Thats what is happening in this area, the cast joints are breaking down and the Ze,s are getting worse.Around here you can get 15 to 35 ohms with a single rod no problem..I think the main benefit with a TT is that you are not relying in an old network for your earth connection..
Say you have a TNS supply (lead sheath) and the sheath rots... you now have a TT, but you don't know it's TT!!
As far as I am aware ,Andy, commercial/industrial supplies always include an earth terminal.TT can be better for domestic, but for commercial, its best avoided. saves the hassle of RCD incomers (since 99% of TPNE board are metal). and RCBOing a TPNE board isnt going to be cheap!).round here, its mostly TNS, newer are TNCS, but there are still a large number of TT, even in the built up area's
fortunately, no requirement. but if there was (and will most likely be in a few years), then it will start getting expensiveAs far as I am aware ,Andy, commercial/industrial supplies always include an earth terminal.Also there is no requirement for overall RCBO ,s on commercial/industrial .
The only reason I can think of for a time delayed main switch is if you are feeding a consumer unit in a detached building. A 100mA time delayed RCD would be needed to ensure a trip if the cable was damaged as current flow to a rod would be insufficient to trip an MCB. Naturally you would have a 30mA RCD locally in the outbuilding. Result - a fault in the outbuilding does not trip the rest of the house and the outbuilding power can be easily restored.Before the 17th edition , we used to put a 100ma Timed delayed RCD as the main switch to protect the lighting, cookers etc and a 30ma on the sockets.Now the 17th edition is out, 30ma on pretty much everything, my thinking is you dont need the 100ma Timed deley?
ohh...in a domestic installation of course
Is that correct?
many thanks
:Y
dual split 17th edition boards with a couple of unprotected yes.JL are these 17th edition boards dual split with a couple unprotected ways? or just dual split?
Didn't think about the metalclad CU - thanks!The only time I now use 100mA S types on a TT system are:
- if the cu is metalclad & the 100mA goes on the tails
- At the head of a submain supplying an outbuilding, if 30mA is used at said outbuilding.
Other than that no need to use 100mA S types if 17th ed dual 30mA cu's are used (not forgetting that circuits on non rcd ways on high integrity cu's need to be rcbo protected).
just goes to prove more that people here know what there doing!Sorry mate - couldn't see the wood for the trees!