Hi Jud,
Sorry, mate, it was the big red writing in the middle of my quoted post - It seemed like you were shouting at me.
When an RCD is used to comply with the disconnection times in table 41.1 (pg 46), a current of 2 x I delta N is typically used. - see Note 2 underneath the table.
If you then look at Table 3A (pg 243), in the second column, it gives the time that a 30mA RCD will trip in, at 60mA (2 x I delta N), as 150mS (0.15 mS)
As we require a disconnection time of 0.07 for our example, this is to slow.
So we go to the next column along - 150mA (5 x I delta N), which gives a trip time of 40 mS (as we know).
As this is within our disconnection time (70mS), then this is the figure we must use.