Hi, I'd appreciate a bit of guidance from the industrial sparks here, I'm out of comfort zone!
The setup is a wood pellet conveyer system with 3 motors driving an Archimedes screw, a vertical lift and another screw.
I've been told the whole lot has run for 3 years without issue
Last delivery the overload for one motor tripped regularly, virtually every two minutes.
This delivery I was called in to watch along with a guy from the company that installed it and it tripped a couple of times in the first 10 minutes and then ran for over an hour without issue. The motor got warm but not so hot I couldn't leave my hand on it. The other guy wanted to increase the trip setting, but I dug in and said if it's worked for years we're not changing that without knowing why it tripped. Obviously I couldn't start pulling things apart during a delivery so I went back later to do some testing.
So far I've done the following: Isolated, got cover of motor wiring box (sounds easy, was ridiculous access!), removed the permanent star connection and did the following tests:
winding 1 = 0.95 ohms
winding 2 = 0.95 ohms
winding 3 = 0.95 ohms
IR between windings and IR of each winding to earth all >300Mohms
Then I tested the wiring between control panel and isolator, and no faults found there either. Today it ran with no load for 30 minutes without issue.
To the extent of my knowledge I'm not seeing an electrical reason it would trip and it seems most likely to me that it was a mechanical issue that was putting higher load on the motor (e.g. oversized wood pellet) and the issue eventually cleared itself.
Are there any more tests I could have done?
Some pictures:
The setup is a wood pellet conveyer system with 3 motors driving an Archimedes screw, a vertical lift and another screw.
I've been told the whole lot has run for 3 years without issue
Last delivery the overload for one motor tripped regularly, virtually every two minutes.
This delivery I was called in to watch along with a guy from the company that installed it and it tripped a couple of times in the first 10 minutes and then ran for over an hour without issue. The motor got warm but not so hot I couldn't leave my hand on it. The other guy wanted to increase the trip setting, but I dug in and said if it's worked for years we're not changing that without knowing why it tripped. Obviously I couldn't start pulling things apart during a delivery so I went back later to do some testing.
So far I've done the following: Isolated, got cover of motor wiring box (sounds easy, was ridiculous access!), removed the permanent star connection and did the following tests:
winding 1 = 0.95 ohms
winding 2 = 0.95 ohms
winding 3 = 0.95 ohms
IR between windings and IR of each winding to earth all >300Mohms
Then I tested the wiring between control panel and isolator, and no faults found there either. Today it ran with no load for 30 minutes without issue.
To the extent of my knowledge I'm not seeing an electrical reason it would trip and it seems most likely to me that it was a mechanical issue that was putting higher load on the motor (e.g. oversized wood pellet) and the issue eventually cleared itself.
Are there any more tests I could have done?
Some pictures: