Now we all know that we cannot transport the earth to a detached garage with TNCS but what do you do in this case.
Main head in house with what looks like TNS head with armoured sheath but with a earth linked as well to neutral, disconnected and checked the Ze on armour of incomer with the neautral disconnected from it, Reading 0.15 ohms, so we established it was probably a TNS so will phone DNO to find out if it is either TNS or TNCS.
Next problem is if it is TNS then no problem with the exporting of the earth but if it is TNCS what do you do as the detached garage houses the gas meter and has 2 gas pipes to the house, both are bonded on point of entry to the house back to the MET the small CCU in the garage has a 10mm bond to the gas as well, so what happens in this situation with TNCS, normally I would break the earth on the supply to the garage and rod the garage on it's own but what happens in this situation.
Many thanks all, Mike.
Main head in house with what looks like TNS head with armoured sheath but with a earth linked as well to neutral, disconnected and checked the Ze on armour of incomer with the neautral disconnected from it, Reading 0.15 ohms, so we established it was probably a TNS so will phone DNO to find out if it is either TNS or TNCS.
Next problem is if it is TNS then no problem with the exporting of the earth but if it is TNCS what do you do as the detached garage houses the gas meter and has 2 gas pipes to the house, both are bonded on point of entry to the house back to the MET the small CCU in the garage has a 10mm bond to the gas as well, so what happens in this situation with TNCS, normally I would break the earth on the supply to the garage and rod the garage on it's own but what happens in this situation.
Many thanks all, Mike.