JJ, there is an alternative way of doing this which would not involve any work on the tails. You say the current cu is full. Well why not pull one of the lighting circuits out of the current cu. Use the space provided to create a small distribution circuit to your new 2 way CU next to it (say 32A/6mm). Redirect the lighting into this and use the extra way for the PV. You might want to consider using a main switch unit and RCBOs.

PS I recently asked a Hager technical guy if RCBOs work backwards.The answer was yes. He did go on to qualify this by saying he couldn't speak for other manufacturers.

 