Alan B
Member
After 2 years use ,I recently notice my bank will not charge above 49.6 volts , the system is an EPEVER hybrid 5KW with 8kw of hoppecke AGM batteries.
I have checked my user and default engineer settings for AGM with EPEVER customer care and all is good .
As far as im aware the batteries have been charging and discharging ok. {until I changed to "utility priority" output a week ago}
when i use a multimeter across the main terminals of inverter that lead to the bank it reads 49.8 v ,this is when the LED display is showing "equalize".
the equalize voltage should be 58.4 v, { "equalize" has been on display constantly for a week} .could this be because....
Im measuring at wrong place or because the bank is connected while testing.
the inverter is faulty
the batteries have bit the dust .
EPEVER have said the need me to return the inverter for testing ,which would be inconvienient .[especially if it turns out to be batteries at fault ]
Im not a sparky but can do basic testing ,any ideas where to go from here please,
I have checked my user and default engineer settings for AGM with EPEVER customer care and all is good .
As far as im aware the batteries have been charging and discharging ok. {until I changed to "utility priority" output a week ago}
when i use a multimeter across the main terminals of inverter that lead to the bank it reads 49.8 v ,this is when the LED display is showing "equalize".
the equalize voltage should be 58.4 v, { "equalize" has been on display constantly for a week} .could this be because....
Im measuring at wrong place or because the bank is connected while testing.
the inverter is faulty
the batteries have bit the dust .
EPEVER have said the need me to return the inverter for testing ,which would be inconvienient .[especially if it turns out to be batteries at fault ]
Im not a sparky but can do basic testing ,any ideas where to go from here please,