looks like a 3 phase to me, a couple of the farms I worked on had exactly the same setup, 11Kv to tx then the supply out, one had a3 phase and the other a single phase, had a very large earth rod planted at the base of the pole. I have been there several times when it was being worked on.

 
If you look in knowledge base I’ve posted a list of UKPN’s standard transformers. 250/500V is the normal for split phase. You can get 2 pole MCB’s rated for 690V but keep an eye on the maximum fault clearance current, the higher the voltage the lower the clearance current.

For a 125A MCCB working on 660V single phase, I used a 4P breaker with two sets of contacts in series. I worked out the maximum fault current and it was scary, 132kA.

 
Here's a pic of the TX... I doubt that it's 3ph as there are only 3 HV conductors...

View attachment 9810

Maybe 4??? 😳
You don't get a neutral on HV, so it's just 3 phases.

The DNO doesn't need to earth the metal frames on the top of posts so often they don't.

So I would agree that there is 3ph running across the top of the pole.

I can't see any more details, but, if there are 3 HV bushings into the Tx, then it's 3ph, & it'll be normal 230/400V.

 