Just been to an optima xm today.
customer complained of the system being locked out.
Battery duff.. got a new battery, did a full reset and walk test everything fine, go to set the system and 2 zones fault
i link the zones and it sets fine, so then check the continuity on the zones and its fine.
to cut a long story short theres 3 PIR's 2 on one zone and 1 on the other. with these removed the system sets but put any 1 PIR on a zone and it wont set. There is 12v at the PIRs and the contacts at each PIR open up when activated. I put these 3 on their own zone, I've got continuity on the zone but as soon as I set it just wont. Any ideas? I've found the technical line and will be going back later today/tonight.
customer complained of the system being locked out.
Battery duff.. got a new battery, did a full reset and walk test everything fine, go to set the system and 2 zones fault
i link the zones and it sets fine, so then check the continuity on the zones and its fine.
to cut a long story short theres 3 PIR's 2 on one zone and 1 on the other. with these removed the system sets but put any 1 PIR on a zone and it wont set. There is 12v at the PIRs and the contacts at each PIR open up when activated. I put these 3 on their own zone, I've got continuity on the zone but as soon as I set it just wont. Any ideas? I've found the technical line and will be going back later today/tonight.