We do some work for a farming estate that has a few cottages dotted about, today's job concerns one of (two I think) their properties along the 'main road' through the village. I say main road, theres quite frequent traffic, but we are definatly 'in the sticks' The job card said the immersion heater kept needing to be be reset, and then stopped working altogether, and the tennent had been recieving shocks off the outside tap initially and then also off the inside plumbing, which were described as something like "not really really bad, but most definately painfull" (I paraphrase) and was wondering if the two were related.... as did I, I was expecting to find a split immersion element and a dodgy TT system.
Alas no..... it was PME (and not a dodgy conversion). Earth loop at the board about 0.25ohms. Ok then switch off main switch and do a proper Ze.... Main earth flashes to the earth bar as I pull it away... odd... definatly something untoward here. Out comes he wandering lead to a temporary spike in the garden, nothing between that and the CU earth bar... at least thats normal, now test the suppliers PME earth.... 193v between that and the physical earth. Time to call the supply authority out, fault engineer turns up, confirms my findings, sends for a lines team, who go up the pole in the field behind the house and check the 16kva "pole pig" sp tx, the same physical ground to neutral earth readings are present there, But disappear when the LV fuse is pulled. Fault enginneer goes to check another property fed from the same tx (which luckily is owned by the same landlord) and comments that the polarity was reversed there... thats odd I think, I did an EICR there last Winter and I wouldn't have missed that!, Did start to think "was it reversed at the cutout, and then swapped back at meter to be presented right at the board" , anyway supply authority chap asks me to just have a check as they arn't really supposed to open up the customer's board. This property is on TT, polarity was correct, but what caused the confusion is that a voltstick lit on the neutral of the concentric supply, think there was about 130v between neutral and TT(earth) and only 94 between live and TT earth. On the previous visit to the property the supply chap had disocnnected the supply from the cutout, and he had done the same in the property where the shocks were experienced (PME earth also disconnected on that one).
Anyone want to hazard a guess what the cause ended up being?
(Nothing to do with the immersion heater, I'll give you that one, that was a dodgy stat, 5 and a half ohms across it when it was closed, and when I pulled the old one apart in the van later on, the contacts had been burning up)
Alas no..... it was PME (and not a dodgy conversion). Earth loop at the board about 0.25ohms. Ok then switch off main switch and do a proper Ze.... Main earth flashes to the earth bar as I pull it away... odd... definatly something untoward here. Out comes he wandering lead to a temporary spike in the garden, nothing between that and the CU earth bar... at least thats normal, now test the suppliers PME earth.... 193v between that and the physical earth. Time to call the supply authority out, fault engineer turns up, confirms my findings, sends for a lines team, who go up the pole in the field behind the house and check the 16kva "pole pig" sp tx, the same physical ground to neutral earth readings are present there, But disappear when the LV fuse is pulled. Fault enginneer goes to check another property fed from the same tx (which luckily is owned by the same landlord) and comments that the polarity was reversed there... thats odd I think, I did an EICR there last Winter and I wouldn't have missed that!, Did start to think "was it reversed at the cutout, and then swapped back at meter to be presented right at the board" , anyway supply authority chap asks me to just have a check as they arn't really supposed to open up the customer's board. This property is on TT, polarity was correct, but what caused the confusion is that a voltstick lit on the neutral of the concentric supply, think there was about 130v between neutral and TT(earth) and only 94 between live and TT earth. On the previous visit to the property the supply chap had disocnnected the supply from the cutout, and he had done the same in the property where the shocks were experienced (PME earth also disconnected on that one).
Anyone want to hazard a guess what the cause ended up being?
(Nothing to do with the immersion heater, I'll give you that one, that was a dodgy stat, 5 and a half ohms across it when it was closed, and when I pulled the old one apart in the van later on, the contacts had been burning up)