Part of the Pylontech CANBus protocol is that the 8 character string "PYLON " (i.e. PYLON and 3 spaces) should be sent as CANBus message 0x35E.
The Solis will fail with the battery name error if the Solis is set to PYLONLV battery type and it does not receive this packet of data periodically.
So all is well if the emulation includes the msg, if not then you may need to select "user defined" from the list of batteries in the Solis menu.
Is their anyway to get the SEPLOS BMS to do this? I get the name Fail error from the RAI-3.0KW 48ES 5G when ever I set PYLON, I have to use user define.
Also does anyone know why I get CAN communication failure to the inverter whenever I plug in an RS485 cable to connect the battery to the PC at the same time as the CAN is active?