Hi Norv
Unfortunatly... NO....
if theres is metal pipe installation within the premises,
then it still needs bonding...
You need to ref On Site Guide. Page 25, point 4.3
I know this is technically the O-S-G re 16th reg's..
But 17th not yet out!
and I don't think this point has changed in 17th.
The other bits I was askin about were just cuz you can get anomalies where..
More than one rising main exists.. In which case I would bond both.
or
A part of the installation pipework disappears under ground again and reappear at another part of the building..
Again this would be bonded in two places origin & where re-appears!
Cant find a reg for the above but NICEIC earth & bonding Snags & Solutions book does mention it on snag 17! "reemerging metallic pipework".
Hope this helps m8.