another question
NWDS
Jun 18, 2008
165
sorry all,
Three pvc insulated cables are connected in parallel, and their resistances are 0.012, 0.015 and 0.008,respectivley,with a total current of 500A flowing on a 240V supply,
A, calculate the current in each cable ( V/R = I )
B, calculate the combined voltage drop over the three cables in parallel,
C, calculate the individual voltage drop over each cable in the paralleled circuit.
I have worked out resistance,
1/0.012 = 83.33 so V/R = I ( 240/0.012 = 20,000 )
1/0.015 = 66.66 so V/R = I (240/0.015 = 16,000 )
1/0.008 = 125 so V/R = I ( 240/0.008 = 30,000 )
am i using the correct formula ( NO ) ???????.
regards NWDS headbangheadbangheadbangheadbangheadbangheadbangheadbangheadbangheadbangheadbangheadbang
i got lost at " 3 pvc insulated cables "
mention PVC to john and he goes a bit giddy] :)
I can always remember the formula much easier as Current = Power / Voltage
thanks Andy, I will copy that so I can go back to it.
NWDS
Applaud SmileyApplaud SmileyApplaud SmileyApplaud SmileyApplaud SmileyApplaud SmileyApplaud Smiley
the answers in me book are
A, 152A,121A and 227A ( all add up to the total current given )
B, 1.82 v
C,1.82 v
NWDS
the answers in me book areA, 152A,121A and 227A ( all add up to the total current given )
B, 1.82 v
C,1.82 v
NWDS
then the book is wrong. VD over all has got to be 240V - there is no other resistances, and the supply voltage is 240V.
C, should there be 3 values? anyway that answer still looks wrong
thanks andy
NWDS
Andy can you explain why you added up the 3 resistences ( I thought they were in parallel ), I understand the rest but not that BlushingBlushingBlushingBlushingBlushingBlushing.
NWDS
Andy can you explain why you added up the 3 resistences ( I thought they were in parallel ), I understand the rest but not that BlushingBlushingBlushingBlushingBlushingBlushing.NWDS
forget what i first said... got the right answers, but in the wrong order... ill work it out again tomorrow, unless someone beats me to it