A few years ago we rewired house for a good customer in Sutton Coldfield, an area known for poor earthing on the network.
We applied for a PME but it was turned down .
After spending a day knocking rods in all over the front garden and getting no readings whatsoever , even with four looped together , two rods at 4 mtrs deep we gave up on that idea .
I decided to use the cable sheath anyway , Ze 14 hms , and fitted a downstream RCD rated at 100mA. I have pictures somewhere.
Anyway , British Gas have been there trying to solve a problem with the boiler cutting out . He's told customer he's taken reading of 200 hms but expected only 100 hms No idea what he was testing !!! But I think he's seen the DNO's sticker on the cut-out and is using it as an excuse to let someone else sort it.
I will return anyway and check that theres still a Ze on the sheath which I'm using as a TT system.
Any thoughts ?
We applied for a PME but it was turned down .
After spending a day knocking rods in all over the front garden and getting no readings whatsoever , even with four looped together , two rods at 4 mtrs deep we gave up on that idea .
I decided to use the cable sheath anyway , Ze 14 hms , and fitted a downstream RCD rated at 100mA. I have pictures somewhere.
Anyway , British Gas have been there trying to solve a problem with the boiler cutting out . He's told customer he's taken reading of 200 hms but expected only 100 hms No idea what he was testing !!! But I think he's seen the DNO's sticker on the cut-out and is using it as an excuse to let someone else sort it.