Can I ask a quick question, if you install down lighters in zone 1 can they be 230v providing the lighting circuit is protected by a RCD and the down lighters are suitable for zone 1 and are at least IPX4?
CorrectThanks for clearing that up, saw the bit about IP in the regs and would need to increase to IPX5 with jets of water. So I presume that you would just connect the 1.5 T&E switch return from the junction box to the first downlighters connection blocks and then loop to the next?
Correct
When you get into the real world you will find many of the lights have a cheap, small connector with no earth terminal that you would be lucky to get 1 tw&e in, let alone 2.
The best way to tackle this is to wire a short length, 300mm or so of .75mm flex to the light (2 core may be ok if there is no earth terminal) and wire this to a JB where the tw&e connect in. This also helps to stop some of the cheaper fittings pulling over due to the weight of the tw&e's.
whats that Noz?Or instead of wiring into a JB wire them into a Click Flow connector
http://www.scolmore.com/flow.htmlwhats that Noz?