A good tip when you can not find any tables, or when you are onsite without your reference materials is to calculate the max Zs.
BS 3871 are from around 1965, they are split into type 1, type 2 and type 3. Type 1 allows 4 times the breakers rating type 2 is 7 and type 3 is 10.
So if we take a 15amp type 1 as an example we have 15x4 giving us 60, 230/60 = 3.83 max Zs.