sounds like a right mess!
it is 2 core mate, prob off a jb under the floorshe'd be a bit mad not to go for it. You could always put a seperate shower unit in, but surely that burnt out fuse has demonstrated how dodgy fuse wire can be. Especially if you got a ring with 1mm earth.probably find that there'l be a snapped earth in another socket, reconnect that and reconnect earth to that socket, probably take less time and cheaper then fitting a new one
good post mate thanks just working through it nowtom...(and maselec, badger, fletchflash.....)if you're on tncs... the 6mm bonding needs upgrading to 10mm... no debate.
for tt or tns you need to do the adiabatic equation to decide if 6mm is big enough to carry the fault current (or upgrade it anyway to comply)
it's reg 543.1.3..... i can't do the symbols typing here, but if you're having trouble doing or understanding this
post up the pfc.... and the main fuse type, and someone will calculate it for you.
you can use this equation as a reason for not changing an earthing conductor or bonding....(only for tt or tns tho').... and it's all in the brb.