hello chaps,

would 2.5 be ok for a 10m run through house to box into swa for 15m to run a lamp post style garden light? she may also want another pir run off the same circuit.

thanks

 
Wattage? grouping factor? thermal insulation? Type of protective device? Cable buried underground?

Sorry Paul total overkill I know just been doing an assignment for 2391-20 and all these are factors that seriously derate cable sizes.

On the face of it assuming lamp wattage of 500W for your average TH fitting I would say 2.5mm would be more than adequate.....

 
If you assume 500watts circuit design and clipped direct you could use 1mm cable!

Supply voltage = 230 Volts

Ib - design current = 2.2 Amps

Protective device type = MCB typeB

In - protective device rating = 6 Amps

Length of run of cable = 25 meters

Power factor = 1

Cable Type : General purpose PVC - Multicore

Installation Method : Single-core or Multi-core cables Fixed on (clipped direct), or spaced < 0.3 x cable diameter from a wooden or masonary wall

method C

Ambient temp = 30

 
Last edited by a moderator:
Shouldn't that be 3% as its a lighting circuit?
Yes you are correct it should be 6.9 my fault, and thanks for picking it up I will edit accordingly ;)

 