Hi,
A 230v 6KW single phase load is supplied by single core pvc cables in high impact pvc conduit fixed to the surface of a brick wall over a distance of 20 metres. The circuit is protected by a C Type CB. The temperature is 35 degrees C.
Determine
a) Design current
B) Installation method
c) CB rating
d) Correction Factor
e) Minimum cable rating
f) Minimum cable size
g) Volt Drop
a) 6000/230 = 26A
B) Reference Method B (From OSG P52)
c) 32A Type C
d) 0.94 (Page 124 OSG)
e) 32/0.94 = 34A
f) 6mm cable is good for 38A (Ref Method B)
g) 7.3 x 32 x 20
1000
= 4.672V which is less than 5% allowed for power circuits
Can someone let me know if ive done it right
Thanks in advance
Matt