Fault appears to be cooker circuit (40A) - 6mm
gas hob - plug-in single oven.
two double sockets in kitchen fed from cooker socket in 2.5
one is behind washing machine.
tests narrow fault to this cct.
"can you pull washing machine out please?"
see double socket, and this plug:
http://i316.photobucket.com/albums/mm323/kmelectric/IMG_0237.jpg
ooh!! looks like it might have got a bit warm??
have you seen a 2 pin plug, which looks like a 3 pin plug?
http://i316.photobucket.com/albums/mm323/kmelectric/IMG_0236.jpg
The other pin didn`t stay in the socket - it wasn`t there at all.
The landlord had responded to a request for more sockets, by plugging a 4 way extension lead into the double socket, and letting the tenants put their washing machine, dishwasher and tumble dryer on the 4 way.
This is the plug on the 4 way.......
http://i316.photobucket.com/albums/mm323/kmelectric/IMG_0235.jpg
Be afraid. My customer was.
Oh, yes. Same house had 2.5 radial on 32A mcb. Split load board installed recently. No labelling, and only item on rcd side is leccy shower.
And the BAD news?????
The tenants are my daughter, and three grandkidsX(X(X(X( X(
I`m hoping to meet the landlord.........................
gas hob - plug-in single oven.
two double sockets in kitchen fed from cooker socket in 2.5
one is behind washing machine.
tests narrow fault to this cct.
"can you pull washing machine out please?"
see double socket, and this plug:
http://i316.photobucket.com/albums/mm323/kmelectric/IMG_0237.jpg
ooh!! looks like it might have got a bit warm??
have you seen a 2 pin plug, which looks like a 3 pin plug?
http://i316.photobucket.com/albums/mm323/kmelectric/IMG_0236.jpg
The other pin didn`t stay in the socket - it wasn`t there at all.
The landlord had responded to a request for more sockets, by plugging a 4 way extension lead into the double socket, and letting the tenants put their washing machine, dishwasher and tumble dryer on the 4 way.
This is the plug on the 4 way.......
http://i316.photobucket.com/albums/mm323/kmelectric/IMG_0235.jpg
Be afraid. My customer was.
Oh, yes. Same house had 2.5 radial on 32A mcb. Split load board installed recently. No labelling, and only item on rcd side is leccy shower.
And the BAD news?????
The tenants are my daughter, and three grandkidsX(X(X(X( X(
I`m hoping to meet the landlord.........................