I Have just removed the wiring from a 900 sq ft unit with a 900 sq ft mezzanine and I now have a fresh start. ( I had my doubts about the pvc insualtion tape holding it together!)
Could someone please clarify the following points:
1. As I understand it RCDs are not mandatory in a commercial application. However I intend to install 2 Redring instant water heaters each rated at 2.5kW. I was planning to supply each unit with 2.5mm2 T & E protected by a 16A mcb with the heater connected to a 13A rcd fused spur since I am concerned about water and the manufacturer supplies these with a 13A plug. Am I also right in thinking that the pipe work should be earth bonded throughout.
2. Have I interpreted the tables correctly that 2.5mm2 T & E inside trunking (plastic) is derated to 21A current carrying capacity and therefore if used in a ring main then a 20A mcb is the most appropriate choice?
I am trying to make sure that I get this roughed in correctly beforew I get it tested and inspected. Many thanks
Could someone please clarify the following points:
1. As I understand it RCDs are not mandatory in a commercial application. However I intend to install 2 Redring instant water heaters each rated at 2.5kW. I was planning to supply each unit with 2.5mm2 T & E protected by a 16A mcb with the heater connected to a 13A rcd fused spur since I am concerned about water and the manufacturer supplies these with a 13A plug. Am I also right in thinking that the pipe work should be earth bonded throughout.
2. Have I interpreted the tables correctly that 2.5mm2 T & E inside trunking (plastic) is derated to 21A current carrying capacity and therefore if used in a ring main then a 20A mcb is the most appropriate choice?
I am trying to make sure that I get this roughed in correctly beforew I get it tested and inspected. Many thanks