Hello NAT!Ok, this is where I'm getting confused...how is it decided what size the Main Fuse should be then? You obviously don't just add up the breakers that are in the installation, 'cos 9 times out of 10, the total would always exceed the MF size
That's why I was allowing for a 50A mcb in the main CU to cover the circuits in the garage CU:
32A - ring main
10A - rear garden lights
6A - front garden lights
6A - garage lights
Doesn't the mcb for the garage (in main CU) have to be rated higher than the highest mcb in the garage CU? <- hope that makes sense to you!!!
Obviously I was WAY off the mark, which I've now realised, but TBH, if I was to do this again (which I hope I will at some point!), I'd still be a bit stuck as to the size of fuses to use.
What additional info is required? Sorry to go on about this, but it's doing my head in and I really need to understand [thoroughly] what I'm doing, otherwise I don't see the point...
You've all been a great help so far - much appreciated.
Nat
This I dont think will be a "quicke" sounds like we need a "Longie" here to get a few basics to gel a bit more in your mind?
GARAGE:
What ACTUAL items of equipment are you going to connect in your garage???
why do you pick a 32A ring main?
Are you running around 2.5Kilowatts of lighting on you rear light circuit? (10a x 230v =2300watts!!!)
HOUSE:
How big is the property
e.g. No or rooms approx floor space?
How many people are living there ?
Are there any specific/unusual requirements.?
e.g. I have a customer who does ceramic design work with a small electric Kiln!! which ramp the old max demand up a bit!!!
DIVERSITY:
You said in an earlier post you had calculated demand with "diversity" to be 159amps???
How did you calculate this??
It may help us to explain a bit where you are going wrong.
I will add a bit more latter rather than making a ridiculously long post??